  #71  
Old 2019-03-20, 03:15 PM
TDIGUY TDIGUY is offline
Member
Regular User
 
Join Date: Dec 2018
Location: Outside Windsor
Posts: 59
Default

Quote:
Originally Posted by BartBandy View Post
Table 9.7.2.3: 5. Bedrooms: Unobstructed glass area of 5% of area serviced

Section 9.9.10.1 (b) Unobstructed open portion of 0.35m2 (3.8sqft) with no dimension less than 380mm (15in)

Translation: Bigger windows than you were planning for a basement.



Fun times.
If my measurements are right at 18x30 I would be 3.75 sq.ft of the 3.8
Hopefully it is a bit bigger so I hit the 3.8 sq.ft and I should be OK.
If I need to hit 5% as well I will have issues as I would need to double the window size at least.
Reply With Quote
  #72  
Old 2019-03-20, 04:27 PM
BartBandy BartBandy is offline
Senior Member
Regular User
 
Join Date: May 2010
Location: Ontario/Nobleton
Posts: 1,662
Default

Quote:
Originally Posted by TDIGUY View Post
If my measurements are right at 18x30 I would be 3.75 sq.ft of the 3.8
Hopefully it is a bit bigger so I hit the 3.8 sq.ft and I should be OK.
If I need to hit 5% as well I will have issues as I would need to double the window size at least.
Is that the size of the opening created when the window is open?
__________________
Reply With Quote
  #73  
Old 2019-03-20, 04:32 PM
TDIGUY TDIGUY is offline
Member
Regular User
 
Join Date: Dec 2018
Location: Outside Windsor
Posts: 59
Default

Quote:
Originally Posted by BartBandy View Post
Is that the size of the opening created when the window is open?
Yes, here is a picture of the window style, this one currently opens down but I can flip them the other way as well and they have a hinge lock to hold them in the open position. I am going to confirm the size tonight.
Attached Thumbnails
Click image for larger version

Name:	20181127_224710.jpg
Views:	109
Size:	139.1 KB
ID:	14659  
Reply With Quote
  #74  
Old 2019-03-20, 05:09 PM
BartBandy BartBandy is offline
Senior Member
Regular User
 
Join Date: May 2010
Location: Ontario/Nobleton
Posts: 1,662
Default

If it opens down, I'm not sure how that works for egress.
__________________
Reply With Quote
  #75  
Old 2019-03-20, 05:30 PM
TDIGUY TDIGUY is offline
Member
Regular User
 
Join Date: Dec 2018
Location: Outside Windsor
Posts: 59
Default

Quote:
Originally Posted by BartBandy View Post
If it opens down, I'm not sure how that works for egress.
It can be flipped to open up. I just haven't changed them all yet.
Reply With Quote
  #76  
Old 2019-03-20, 06:00 PM
good2know's Avatar
good2know good2know is offline
Senior Member
Regular User
 
Join Date: Sep 2010
Location: Ottawa
Posts: 5,787
Default

Found this:

Basement Exit Window for Bedroom Requirements
Although I have written a number of articles on this subject I still come across Realtor’s who will offer their opinion on Requirements for Basement Windows based on “hearsay” vs the Ontario Building Code. This type of confusion is encountered a lot when individuals, without any formal training, start advising home buyers on Building Code requirements when purchasing a home.

The biggest mistake I find people make is stating that each bedroom requires an “EXIT WINDOW”. This is simply not true. Although there are requirements for light and ventilation, this is not part of exit requirements.

The requirement for a properly-sized bedroom window has been around since 1980 and subsequent code changes since then have made it even easier to understand how a bedroom egress window is defined. As with any building project, a proper building permit is required and your drawings will be required to show location and size of windows. There is always some interpretation involved in Ontario Building Codes and Fire Codes, so to be safe consult with the Inspection Department and Fire Department prior to starting construction.

National Building Code of Canada
The National Building Code of Canada (NBCC), on which the Provincial Codes are based, has very clear requirements as it relates to bedroom windows and how the bedroom window serves three distinct purposes in the home:

Light (at least five per cent of the floor area served)
Ventilation (at least 0.28m or 3 ft or an adequate year-round mechanical ventilation)
Emergency Escape: An Emergency Escape requires that each bedroom must have a door that leads directly to the exterior of the building or have a properly-sized egress window that can be opened from the inside without the use of keys, tools, hardware or special knowledge (unless this bedroom has a sprinkler system installed).
Ontario Building Code article 9.7.1.2. establishes the general requirement that all bedrooms must have at least one window that is large enough to be used as an exit in an emergency. The specific requirements are as follows:

Ontario Exit Window Basement

Except where the suite has a sprinkler, each bedroom or combination bedroom shall have at least one outside window or exterior door operable from the inside without the use of key, tools or special knowledge and without the removal of sashes or hardware.
The window referred to in Sentence (1) shall provide and unobstructed opening of not less than 0.35 m (542 in or 3.8 ft) in area with no dimension less than 380 mm (15 inches), and maintain the required opening during an emergency without the need for additional support.
If the window referred to in Sentence (1) is provided with security bars, the security bars shall be operable from the inside without the use of any tools or special knowledge.
If a window well is required, it must be out from the window at least 550mm (about 22″) to provide safe passage. Awning style windows for example opening into a window well typically won’t work because they tend to obstruct clear passage unless the window well is unusually large.

It is further recommended that the bottom of any egress window opening or sill not be higher than 1.5m (5 feet) above the floor. Now this can be somewhat challenging for any bedroom in a basement, so some means of built-in furniture below the window to assist in the event of an emergency is required.

Egress Windows or Doors for Bedrooms (9.9.10.1)
Except where a door on the same floor level as the bedroom provides direct access to the exterior, every floor level containing a bedroom in a suite shall be provided with at least one outside window that,
is openable from the inside without the use of tools,
provides an individual, unobstructed open portion having a minimum area of 0.35 m (3.8 ft) with no dimension less than 380 mm (15 inches), and
maintains the required opening described in Clause (b) without the need for additional support.

Except for basement areas, the window required in Sentence (1) shall have a maximum sill height of 1,000 mm (39 inches) above the floor.
When sliding windows are used, the minimum dimension described in Sentence (1) shall apply to the openable portion of the window.
Where the sleeping area within a live/work unit is on a mezzanine with no obstructions more than 1,070 mm above the floor, the window required in Sentence (1) may be provided on the main level of the live/work unit provided the mezzanine is not more than 25% of the area of the live/work unit or 20 m, whichever is less, and an unobstructed direct path of travel is provided from the mezzanine to this window.
Where a window required in Sentence (1) opens into a window well, a clearance of not less than 550 mm (22 inches) shall be provided in front of the window.
Where the sash of a window referred to in Sentence (5) swings towards the window well, the operation of the sash shall not reduce the clearance in a manner that would restrict escape in an emergency.
Where a protective enclosure is installed over the window well referred to in Sentence (5), such enclosure shall be openable from the inside without the use of keys, tools or special knowledge of the opening mechanism.
Tthe required window size for egress is the same between the National Building Code and the Ontario Building code. Window well requirements are the same as well.

The significant difference between the National and Ontario codes is that a means of egress is required for each bedroom with the National Building Code, while only one means of egress per level is required with the Ontario Building Code. Also, the National Building Code requires the sill height from the floor to be no more than 1,500 mm (59 inches), while the Ontario Building Code requires the sill height to be no more than 1,000 mm (39 inches).
Reply With Quote
  #77  
Old 2019-03-20, 06:26 PM
TDIGUY TDIGUY is offline
Member
Regular User
 
Join Date: Dec 2018
Location: Outside Windsor
Posts: 59
Default

I think I read the same article earlier as well. Going to measure shortly and see where I stand on size.
Reply With Quote
  #78  
Old 2019-03-20, 07:38 PM
TDIGUY TDIGUY is offline
Member
Regular User
 
Join Date: Dec 2018
Location: Outside Windsor
Posts: 59
Default

Ok, checked the window size and they are 30x20 for the opening which works out to 4.16 sq.ft. so the meet code for an egress.

Now on the other side with the beam, I got up to take a look and the joists coming from the beam side just barely pass the beam so there is only maybe 1" sitting on the ibeam so I can not just remove the beam but I could possibly slide the ibeam over to replace it. I may look into the brackets to tie the beam into the ibeam and bolt into the joists for support to get rid of the blocking they did.
Reply With Quote
  #79  
Old 2019-03-21, 08:28 AM
good2know's Avatar
good2know good2know is offline
Senior Member
Regular User
 
Join Date: Sep 2010
Location: Ottawa
Posts: 5,787
Default

Great news on the windows
Reply With Quote
  #80  
Old 2019-03-21, 08:35 AM
TDIGUY TDIGUY is offline
Member
Regular User
 
Join Date: Dec 2018
Location: Outside Windsor
Posts: 59
Default

Quote:
Originally Posted by good2know View Post
Great news on the windows
Definitely helps not having to cut the foundation!
Reply With Quote
Reply

Bookmarks

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
ESA inspection for basement renovation peter919191 Ottawa 9 2012-06-12 10:14 AM
looking for a good basement renovation company xox2011 Ottawa 1 2011-11-23 09:13 AM
Fall and Winter Basement Renovation Recommnedations R.F.D. Burlington 9 2011-10-13 10:55 AM
Quick Question about Basement renovation Mr.NewHomeOwner Building and Construction 4 2011-06-08 12:15 PM
Basement renovation, any recommended contractors? htsource Burlington 8 2011-02-25 03:24 PM



All times are GMT -4. The time now is 01:42 AM.



Copyright © PHAND Corporation
This document may not be used elsewhere without the expressed written consent of PHAND Corporation.
*** There is no association between this website and any builder. ***

Powered by vBulletin® Version 3.8.10
Copyright ©2000 - 2021, vBulletin Solutions, Inc.